amp meter installation

Discussion on general flowbench design
jfholm
Posts: 1628
Joined: Fri Feb 19, 2010 7:36 pm
Location: Grantsville, Utah 45 min west of Salt Lake City

amp meter installation

Post by jfholm »

I need help from you electrical guys here. I am going to run 110 motors in series so I can use 220v supply. I want to install amp meter(s) to monitor the amps I am drawing. I have seen some dual meters on ebay that measure both volts and amps and are digital display. Do I need to run two amp meters? One for the black leg and one for the red leg?

John
86rocco
Posts: 292
Joined: Thu Mar 04, 2010 9:01 pm

Re: amp meter installation

Post by 86rocco »

As long as everything is running off of 220V, and no current is flowing through the neutral, i.e. it'll run with the neutral (white) wire disconnected, then one ammeter will suffice.
Brucepts
Site Admin
Posts: 1862
Joined: Fri Jan 08, 2010 3:35 pm
Location: Pennsylvania
Contact:

Re: amp meter installation

Post by Brucepts »

Linky to said meters?
Bruce

Who . . . me? I stayed at a Holiday in Express . . .
jfholm
Posts: 1628
Joined: Fri Feb 19, 2010 7:36 pm
Location: Grantsville, Utah 45 min west of Salt Lake City

Re: amp meter installation

Post by jfholm »

86rocco wrote:As long as everything is running off of 220V, and no current is flowing through the neutral, i.e. it'll run with the neutral (white) wire disconnected, then one ammeter will suffice.
I was just going to wire it per schematic that was just posted last week? where it showed using 110 motors in series. Keep in mind I do not have a great electrical back ground. One time when my Dad was punishing me he said "GO GET A SWITCH!" and it took me an hour to get back from Home Depot. :lol:
jfholm
Posts: 1628
Joined: Fri Feb 19, 2010 7:36 pm
Location: Grantsville, Utah 45 min west of Salt Lake City

Re: amp meter installation

Post by jfholm »

Brucepts wrote:Linky to said meters?

HUH? :D
Brucepts
Site Admin
Posts: 1862
Joined: Fri Jan 08, 2010 3:35 pm
Location: Pennsylvania
Contact:

Re: amp meter installation

Post by Brucepts »

You said looking at them on ebay

I asked for the linky? Or for you old guys link to meters?

Would be a nice sales tool for on a demo flowbench to be able to show the amps running.
Bruce

Who . . . me? I stayed at a Holiday in Express . . .
Malvin
Posts: 451
Joined: Sat Feb 27, 2010 12:50 am
Location: Pennsylvania

Re: amp meter installation

Post by Malvin »

Brucepts
Site Admin
Posts: 1862
Joined: Fri Jan 08, 2010 3:35 pm
Location: Pennsylvania
Contact:

Re: amp meter installation

Post by Brucepts »

Thanks I was to lazy to look for myself :oops:

Looks like something else to add to my flowbench to try out.
Bruce

Who . . . me? I stayed at a Holiday in Express . . .
jfholm
Posts: 1628
Joined: Fri Feb 19, 2010 7:36 pm
Location: Grantsville, Utah 45 min west of Salt Lake City

Re: amp meter installation

Post by jfholm »

yes the "linky's" ;) Malvin used show what I was looking at. The second link shows something along the line of what I want to do. As Ed mentioned the way it will be wired I think one meter will be fine and easy to install, Thanks guys!

John
jfholm
Posts: 1628
Joined: Fri Feb 19, 2010 7:36 pm
Location: Grantsville, Utah 45 min west of Salt Lake City

Re: amp meter installation

Post by jfholm »

Here is something interesting, a 10 gauge wire in romex, as in a 10/3 cable has an amp rating of 30 amps at a room temp of 86º f. If you take the same 10 gauge wire in a single conductor not in conduit or bundled as in romex has an amp rating of 58 amps at the same room temp. I had no idea it would be that much difference. :o