by Tony » Sun May 18, 2008 9:04 pm
Great thread Daniel.
There are several important aspects to weigh up when choosing between transducer types.
The first is sensitivity. As 86roccol has pointed out, use the lowest pressure range you can possibly get away with. The electrical output from these sensors is always extremely small, and that means trouble. For instance, if you are only using 5% of the total available pressure measurement range, any temperature drift or zero errors will appear twenty times worse than if you could have used the whole available pressure measurement range.
If measuring only 3Kpa, a 100Kpa range transducer is definitely not a good idea, a 10 Kpa transducer makes a lot more sense.
At the other extreme, these sensors can be permanently damaged by overpressure. If your air blower can reach 120+ inches of completely blocked flow air pressure, one unhappy day, your pressure transducer might see all of that. Make absolutely sure your transducer is rated well above the worst possible overpressure accident that can possibly occur.
The third factor is temperature stability. The manufacturer can do this a lot more accurately than you can. A temperature corrected sensor will cost slightly more, but is absolutely necessary.
Read all the fine print in the specifications. Some transducers can be many times better or worse than others, in various subtle ways.
How many bits a/d resolution ? Realistically ten bits (1024 steps) should be more than sufficient, because the accuracy, noise, and long term stability of the whole system is not going to be better than 0.1% anyway.
A far more fruitful approach to higher pressure resolution is to average a large number of separate readings in software. (statistical averaging) This averages out a lot of the random reading errors due to acoustic noise, electrical noise, and air turbulence. It will provide far more stable high resolution readings than trying to read incredibly small pressure changes directly.
As to differential pressure transducers, the one I really like best so far is the Sensirion SDP2000 discovered by Bruce.
It requires no external amplifier, it can drive an a/d directly with a 4 volt output signal. It is particularly well temperature compensated, and has a full scale pressure range of only 14 inches. It is totally immune to overpressure damage (>400+ inches) because of the highly unusual method of operation. Accuracy is 0.2% and it is available with either a linear or square root output.
These sensors are certainly not cheap at around $90, but they require no circuit board or external amplifier, which offsets some of the high cost.