by 86rocco » Mon Jan 16, 2006 5:49 pm
It's not quite as simple as that because as the fluid rises in the tubing it drops in the well and the measurement need to be from the surface of the fluid in the well to surface of the fluid in the tubing. Fortunately, this happens in an easy to predict and calculate fashion based on the relative areas of the tube and well. If for example, your manometer tubing is 5/16" I.D. and your well is 1 1/2" I.D. a rise of 36" is the tubing would result in a drop in the well of 1.5625" for a total of 37.37.5625". Now on this manometer if you were to use a normal yard stick, with the zero at the static level, you would need to multiply your reading by 1.0434 =(37.5625/36). I got those numbers by plugging 5/16, 1 1/2 and 36.0 into the manometer worksheet in and simply made the scale vertical height the same as the scale length.
If you wanted to, there nothing to prevent you from creating your own scale which takes this into account and reads directly in fps. The inclined manometer spreadsheet I already refered you to is a good starting point, that scale working in a similar manner to a fps scale. For example, using the same numbers as before, a 37.5625" WC reading from a pitot tube corresponds to 405 fps, multiply 405 by the percentages on the scale and you'll have a fps scale.