by Tony » Wed Apr 15, 2009 6:56 pm
Here are a few things to think about.
Firstly, the test pressure MEASUREMENT SYSTEM should never be used to control the test pressure. It is a very bad idea.
The pressure CONTROL SYSTEM should be kept entirely separate.
Try to imagine what happens if the pressure transducer goes funny or starts to drift. The test pressure could then wander all over the place, but the DAQ wiill tell you it is holding solid at the set 28.00 inches.
If the measurement system is completely independent to the control system, and it is telling you the test pressure is holding steady at the correct set pressure, then it is. And you can be entirely confident that the whole system is stable and behaving itself. The aerospace and biomedical people do this all the time with mission critical or life support control systems. It a the golden rule never to be broken.
Next we need a PID control system that must be tunable to suit the blower motor characteristics. Three possible ways to do it. You can use the main computer which requires an extra DAQ pressure input channel and some type of analog, PWM, or serial data output to control the blower motor power. Or buy a commercial PID module which will not be cheap. Or lastly use two resistors, a capacitor and a one dollat chip to build your own PID system which will work every bit as well, if not better than a software based PID system.
Last thing we need is the power control module to be able to control ALL the motors together. That may be 30 to 100 Amps ?? All the motors need to be controlled because the control system needs to adjust the flow from absolutely flat out, right down to completely blocked flow, and still hold constant set test pressure. No motor switching allowed, it must be continuous smooth control all the way. That is a heck of a lot of power to control.
Only practical way to do it is by using the usual mains phase control system that everyone else uses. That is simple, although the high power switching devices and the required heat sink will be fairly large and expensive however it is done. The really big issue here is that this power switching module will be directly connected to the mains supply and all of it will be electrically alive, and potentially lethal if touched.
That worries me greatly, if this is to be a home built Forum project. Buying a commercial router speed control sealed entirely in a plastic box with a plastic knob is one thing. Constructing something vastly larger with exposed metal parts that are alive, for Forum members to construct themselves could be rather dangerous.
It is a bit like guns, explosives, and very dangerous chemicals. Each of us might feel entirely confident doing it themselves.
But suggesting that someone else (you do not really know well) handle these same very dangerous items is extremely unsettling.
Supplying a PTS 100 Amp power module all built up and ready to go will be expensive, because the parts to build it will be very expensive, way beyond what most here would considder being a viable budget DIY home project.
The last problem is this electrically alive power module needs to be connected to the computer output port, so it can be controlled.
That also requires full electrical isolation which needs to be done properly, because your life depends on it being done properly. It all adds to the cost.
The last hurdle to overcome is that mains phase control needs circuit timing changes if operating at either 50 Hz or 60 Hz. It absolutely must be accurately synchronised to every mains cycle, so the phase control system must be built into the power control module. A computer has absolutely no idea what the mains supply is doing at any instant, so that part of it cannot really be done in software without providing another mains reference input port. It all add to the cost and compleity.
O/k sorry for all the doom and gloom, but this ain't at all easy. I have been thinking about all this now, for a very long time.
My current best approach for this would be to provide a completely built up independent test pressure control module. No computer required (sorry Rick !)
It would be completely analog, with no software at all. That cuts down the cost and complexity significantly. It might be just a large plastic box that connects into the power cable going to all the motors to control the power.
It would have a plastic barbed fitting to connect an air pressure sensing line to the bench to sense the test pressure. That overcomes all the difficult mains isolation problems, and ensures absolute electrical safety in a very simple way. There would be an insulated plastic knob on this box to set, and then automatically maintain that test pressure constant by varying to power to the motors.
This approach is the best I have come up with so far, that combines electrical safety, a control system completely independent of the measurement system, simplicity, and lowest cost. This may not be at all what people want or expect, but I am wide open to any other ideas or suggestions.