by trader » Fri Aug 25, 2006 12:46 am
Larry, I think you already understand this, so I'll give my take on the issue.
The commercial avering pitot's have a minimum and maximum (CFM) operating range for the different pipe sizes. (like orifices) They also have a operational range in differential pressure (D/P in. W.C.). With the orifice, you are working in a D/P % range of 100%, for multiple orfices.
It is basically the same with the pitot (in my mind).
The min and max cfm flow ranges for the pipes(commercial averaging pitot) are 1.5" 10 to 300 cfm. The 2" pipe is 20 to 500 cfm. The 3' pipe is 40 to 800 cfm. In a 1.5" pipe, the operating range is 0.38 to 115 (D/P in. W.C.) and in a 2" pipe it is 0.75 to 75 (D/P in. W.C.) and in a 3" pipe it is 0.39 to 35 (D/P in. W.C.) to match the cfm numbers listed. These numbers are rounded out and air @ 60f & 14.7 psia.
The obvious concern, is, that if you are using a water (incline) manometer. (115"wc, 75"wc, 35"wc) Even with some commercial electronic (D/P) manometers that have that high a range, they will have less resolution to the right of the decimal point. Look at the differential pressure you have to generate to cfm range.
I feel the 3" pipe has a more realistic D/P and cfm range for a single pipe system, with electronics. What did he say? KISS.....keep it smart & simple.
This may not be entirely right, but just how I see it...
trader
Changing one thing, changes everything...